This how-to describes how to connect an IDX70 drive from maxon with ctrlX CORE as a step-by-step guide.
It adresses customers using maxon drives as well as ctrlX OS devices, such as controls in their machines or installations.
Requirements
Hardware
ctrlX CORE X3 with ctrlX OS version 1.20 (or higher) pre-installed
Software installed on ctrlX CORE X3
PLC basic app (or higher/with add ons)
Software installed on engineering PC
ctrlX I/O Engineering and PLC Engineering (parts of ctrlX WORKS)
For operation of ctrlX PLC, ctrlX EtherCAT Master and ctrlX Motion app an adequate software license is required!
Export of the ESI file for EtherCAT
Start EPOS Studio
Connect IDX Drive via USB with the EPOS Studio
Set up Your IDX via the Startup Wizard in EPOS Studio
Startup Wizard Note down the resolution of your IDX drive during the configuration.
Resolution of IDX Tune the IDX Motor via the Autotune Function.
IDX Controller auto tuning Open the "Object Dictionary" tool.
Right-click on any line in the "Object Dictionary".
Select "Export ESI File".
Export ESI File from object Dictionary