We are seeing a case Where S-0-0047 and P-0-0047 are differing when scoping. S47 is correct but p47 bounces +- 100 degrees occasionally. This causes a fault of course. I cant figure out why they would be different values.Β
Difference in S-0-0047 and P-0-0047
Best reply by Rannug
The "Sβ0β0047, Cyclic position control: Command value" cyclically transmitted/written by the control unit is displayed in the parameter "Pβ0β0047, Cyclic position control: Active command value". When reading Sβ0β0047 (e.g., oscilloscope or drive telegram), the drive provides "Pβ0β0434, Position controller: Position demand value", that takes effect directly at the position controller input.
Β
2 replies