Ctrlx Motion Interface

Hello All, 

When I try to use the ctlx Motion Interface on version 2.4 PLC I can only get the first 2 axies to appear. There is a fault in the motion interface program with error ID 4 ACCESS_ERROR, Error Ident CXA_TABLE, Additional info 16#80010001. When I try to reset the error it presists and does not get out of state 4, STATE_INIT_RUN. 

Any ideas? 

Best reply by Jochen_Mueller

Hello

it is a known bug and solved with new MotionInterface libs available at the colaboration room. After installing the libs at the library repo you have to adjust the placeholder versions manual.

With this the motion interface can be initialized also you have axis name longer than 10 characters.

LINK

PS:

Please keep in mind that there is another bug that prohibit the writing of dynamic sync values if you have axis names longer than 10 character. This will be solved with the version 2.6.

Regards

Jochen