- The FSoE-Connections are defined by the *Modules*.xml file.
- During import of the ESI Files you place both files in the same directory and select BoschRexroth_ctrlX_SAFETY_SAFEX_C12_C15_ECAT.xml. During the import it automatically refers and includes the Modules part.
- The error code "0x001E: Invalid Input Configuration" is not related to types (byte width) of FSoE connections but to the configuration of the SAFEX-C.1x in relation to the EtherCAT configuration defined on the ctrlX CORE (EtherCAT-Master). The configuration is only accepted during start-up of the EtherCAT-Master, if all slots of the SAFEX-C.1x in EtherCAT configuration defined in ctrlX IO Engineering and transfered to the ctrlX CORE are identical to the effective EtherCAT-configuration inside the SAFEX-C.1x.
- The number of populated FSoE-Master-Slots (up to 32) and their ID in the EtherCAT-Master-configuration must be the same as the defined FSoE-Slaves inside the SAFEX-C.1x configuration.
- If the FSoE-Slave check-box (1 slave interface) is selected inside the SAFEX-C.1x configuration the FSoE-Slave-Slot in the EtherCAT-Master-configuration of the ctrlX CORE.
- Any mismatch of the EtherCAT-Master-configuration with the FSoE-Master/Slave related configuration parts loaded inside the SAFEX-C.1x will lead to "0x001E: Invalid Input Configuration".
Let us know whether this helped or not.
Best regards
Your ctrlX SAFETY team