ctrlX SAFETY SDOR properties - what are the number of contacts?

Question from a colleague at DCET:

 

I come back to you regarding the Safety. Our customer would like to have 2 SDOR with both 2 channels each.

See below it is not clear to me what are really available on the ctrlX Safety pointN°7 of the slide:

If I understand correctly the ctrlXsafet has only 1 SDOR with 2 channels.

 

Could you confirm to me?

 

Thank you

 

Best reply by AllAutomation

Dear colleague,

Sorry for the misunderstanding and the delay.

Unfortunately the functionality is exactly as described on the slide:

  • There are two relays with one switch each.
  • Due to the separation of potentials each switch is connected to 2 contact pins at the IO-Connector.
  • For a SIL2 functionality there are two logical SDOR outputs, for SIL3 they need to be used both as a single logical output in dual-channel mode.

In addition I clarified that on the slides according to the terms I used above:

There are different ways to solve this:

  • Check the safety application and the risk analysis! Does it really need SIL3? Very often SIL2 is enough and it is just the fear to have not done the maximum that drives users selecting SIL3 solutions.
  • Check the actuator to be switched by a relay! Does it need less than 2.0 A? If yes, it could be controlled by the 2.0 pp-pn-switching combination of 2 of the 2.0 A outputs.
  • Select an FSoE Safety IO-Device that provides a SDOR output. The FSoE-Master of ctrlX SAFETY can control any FSoE slave.
  • Use two ctrlX SAFETY devices and interconnect them via SMMC (Safe-Master-To-Master-Communication). This provides the capability to distribute the application into different places.
  • Use an SIO-1 extension module from BBH to get 2 addtional relay outputs.
  • Use one of the safety outputs and drive a safety relay extension (e.g. the one we recommend as replacement for SLC-A-UE1x-2FG3D0, see product phase out note)

HTH

 