Multiple Config error of parameter S-0-0240 when setting up power control of drive via I/O

Hi All,

I have an XCS drive which shares it's DC bus with an XMD drive, and wish to control the power as per "2.6. Variant: Automatic load of DC bus to power ON" in the help page /ctrlx-automation-how-tos-qmglrz33/post/suitably-power-on-off-ctrlx-drive-8mT0AfKDChkmhbx

When configuring the XMD drives digtal inputs, setting an digital input to parameter DC Power Bus Control S-0-0240 and attempting to move to operating mode leads to this error: "C0242 Multiple configuration of a parameter ->S-0-0423". I believe this is because the DC Power Bus Control is also set cyclicaly by the ethercat master, however I cannot work out how to deactive this. How can I resolve this error?

ย 

ย 

Best reply by Drives_Uwe

The entry S-0-0240 in S-0-0024 needs to be removed in the XMD drives using the configuration possibilities for cyclic parameters within the EtherCAT control.

ย 

View original