Port forwarding with a Sick Safety PLC via EtherCat EoE

Some additional settings must be made to configure and program a Sick Safety PLC via the EoE communication protocol.

Prerequisites

The instruction is based on:

  • ctrlX CORE V1.18
  • ctrlX CORE EtherCAT Master App V1.18
  • ctrlX PLC Engineering V1.18
  • ctrlX I/O Engineering V1.18

Enable IP forwarding in the ctrlX CORE on the eoe0 connector

  • Open the ctrlX CORE Web interface.
  • Go to the menu point "Settings" and chose the option "Network Interfaces".
  • Activate the switch "Enable IP forwarding".

Enable IP forwarding

Enable IP forwarding in the ctrlX CORE for the XF10 connector

  • Open the ctrlX CORE Web interface.
  • Go to the menu point "Settings" and chose the option "Network Interfaces".
  • Activate the switch "Enable IP forwarding".

Enable IP forwarding of XF10 interface

Setup the I/O configuration

  • Open the ctrlX I/O Engineering
  • Choose Scan for Devices… from the context menu from the item “ethercatmaster”.
  • Double click on the device "Flexi_Soft_Ethercat_Gateway".
  • Activate the checkbox "Virtual Ethernet port".

EoE Settings of the Sick ethercat gateway

  • Activate the window ethercat master and go there to the menu "EoE".
  • Please check if the configuration of the EoE is ok.

EoE Settings of the ctrlX ethercat master

  • The IP address is the same number as the station address. In this example the IP address is 172.31.254.3 and the station address is 3.

Adjustment of Windows 10

  • Now you have to add a route to the windows system.
  • Please start the Dos Box as administrator with the command "cmd".
  • Enter the command "route add -p 172.31.254.0 MASK 255.255.0.0 192.xxx.xxx.xx.

Window adjustment to add a permanent route

Adjustment of the Sick Communication via Gateway

  • Start the program "SafeLogic Desinger 1.8.0 SP1".
  • Edit "com. interface settings".

Start screen of the Sick software

  • Setup the communication settings

Communication settings of the Sick Gateway

  • Then close this dialog and go to the communication settings.
  • Check the communication.
  • If this was successful, activate the profile.

How to check the communication settings of the Sick Gateway

Now you can work with the Sick PLC without an additional external connection.