In this short HowTo article a function block is provided to control a Schunk EGP electric gripper from your PLC program.
Requirements
Electric Gripper with digital IO
ctrlX CORE
Digital Output Module (for example: XI211208)
Apps:
Ethercat Master
PLC
Connection to the gripper
The electric gripper, that is used here, has digital inputs for the close and open commands. Another version of the EGP gripper uses IO-Link, which would result in a different workflow than described here.
Once you have the EtherCAT configuration of your digital output module running (won't be described here), connect the gripper cable to two physical outputs.
PLC function block
Add a funktion block to your PLC project and name it "FB_GripperControl". Inside the variable section add:
FUNCTION_BLOCK FB_GripperControl
VAR_INPUT
bCloseGripper : BOOL; // FALSE = open, TRUE = close
END_VAR
VAR_OUTPUT
bOutOpen : BOOL; // hold gripper open
bOutClose : BOOL; // hold gripper closed
END_VAR
VAR
istate : INT := 0; // state machine for FB
tDelay : TON; // Timer for 15 ms delay
rTrigClose : R_TRIG; // rising edge detector for bCloseGripper
rTrigOpen : R_TRIG; // falling edge detector for bCloseGripper
END_VAR
Then insert the following code to your FB:
// 1) rising/falling edge detector
rTrigClose(CLK := bCloseGripper);
rTrigOpen (CLK := NOT bCloseGripper);
// 2) state machine
CASE istate OF
0: // hold open (default)
bOutOpen := TRUE;
bOutClose := FALSE;
IF rTrigClose.Q THEN
// command: open→close → wait before close
istate := 2;
tDelay(IN := TRUE, PT := T#15MS);
END_IF
1: // wait open – 15 ms pause before open
bOutOpen := FALSE;
bOutClose := FALSE;
tDelay(IN := TRUE);
IF tDelay.Q THEN
tDelay(IN := FALSE);
istate := 0; // go to open state
END_IF
2: // wait close – 15 ms pause before close
bOutOpen := FALSE;
bOutClose := FALSE;
tDelay(IN := TRUE);
IF tDelay.Q THEN
tDelay(IN := FALSE);
istate := 3; // in Geschlossen-Status
END_IF
3: // hold close
bOutOpen := FALSE;
bOutClose := TRUE;
IF rTrigOpen.Q THEN
// Command: close→open → wait before close
istate := 1;
tDelay(IN := TRUE, PT := T#15MS);
END_IF
ELSE
// undefined state → gripper open
istate := 0;
bOutOpen := FALSE;
bOutClose := FALSE;
END_CASE
The state machine inside the FB starts in "Hold open", so that the gripper is open per default. In this state the gripper will receive a signal on the open-input and no signal on the close-input.
Then, when a rising edge on the input variable "bCloseGripper" is detected, the FB will enter a 15 ms pause, which is required by the internal logic of the gripper. In this state both digital inputs on the gripper wont get a signal.
After the pause the FB goes to state "Hold close", where a signal is sent to the close-input and no signal to the open-input.
Then the next falling edge on the input variable "bCloseGripper" will open the gripper again and keep it open.
After the FB is defined, go to your program and create an instance of it and two boolean output variables "bOutCloseGripper01" and "bOutOpenGripper01". If you have several electric grippers connected, create more instances of the FB and more output variables.
VAR
// Gripper Outputs (mapped to digital output module)
bOutCloseGripper01 : BOOL;
bOutOpenGripper01 : BOOL;
// Gripper FB
fbGripper01 : FB_GripperControl;
END_VARThen call the FB inside your program like this:
fbGripper01(bCloseGripper := ,
bOutClose => bOutCloseGripper01,
bOutOpen => bOutOpenGripper01);Finally map the two boolean output variables in your program to the physical outputs on your digital output module. Therefore go down to DataLayer_Realtime in the device tree on the left and select realtime data selectively from ctrlX CORE.
In the pop up window under "Source: Control" on the right side, select "ethercat_master..." (1). Then navigate to the digital output module and select the parameters (2) according to the image below. If you have several grippers, select the parameters for all of them. Then add the parameters to your project with the button in the middle (3) and close the window (4).
Then map the EtherCAT parameters to the variables in your program. Therefore open the output module in the device tree and for each of the parameters double-click on the empty field in the variable column and then click the tree dots, that will appear. There you can select the variables, that should be mapped to the physical ports on your output module. Repeat this for the other grippers, if you have more than one.
Now you can download the program to your control and run it. If you set the input variable "bCloseGripper" of your FB to TRUE, the gripper will close and stay closed. If you set the input FALSE again, the gripper will open and stay open.
Good luck ;)