01/29/2024
ctrlX DRIVE SafeMotion PROFIsafe on PROFINET Shared Devices, with Siemens PLC´s
This how-to gives you some information about the possibilities of the actual supported functions of ctrlX DRIVE with PROFIsafe on PROFINET.
General
Information
  • Support of PROFIsafe Version 2.6
  • Address type 1 and 2
  • PROFIsafe Shared Device
Requirements
  • Runtime FWA-XD1-AXS-V-0402xxx onwards
  • SMO, SafeMotion Speed or higher
  • Type 1: Only the PROFIsafe slave address is checked
  • Type 2: Combination of PROFIsafe master address and PROFIsafe slave address for topologies with more than one PROFIsafe master
Address Type 2
Address Type 2
PROFIsafe shared device
  • for PROFINET topologies with difference master hardware for motion control and PROFIsafe
Shared device
Commissioning Address Type
  • Address Type 1 and 2
Address Typ configuration Drive
S7 Source address
Commissioning Shared Device
Siemens TIA (version 17) Shared CPU only IO´s (315)
  • PROFINET configuration
PROFINET axis configuration
  • Shared Device configuration only IO´s (CPU 315)
Shared device configuration PLC2
Siemens TIA (version 17) Shared CPU F-CPU PROFISafe
PROFINET configuration Safety Axis
  • Shared Device configuration PROFISafe on PROFINET (CPU-F1515)
Shared device Safety configuration PLC1
  • Overview PROFINET Network
4
Safety