ctrlX CORE -> OPC UA server app potentially not compatible with WinStudio OPC UA client.

The note may be interessting to those of  you who wonder .... why a OPC UA setup with a updated device_admin is not working anymore,
                                                                                              .... why the UaExpert testclient is responding unexpeted with ... badhostUnknown
                                                                                               .... why WinStudio OPC UA client is not appropreate anymore to get access to the ctrlX.

At the beginning of ctrlX ( device_admin <=250) unsecure connection/request had been accepted by that ctrlX- device_app. Access to data had been provided and security_features had not been focused on. Nowadays the security token restriction had been implemented inside the device_admin ignoring unsecure requests at all. -> Without securitytoken no answer. (Bad communication .... )

According to that - either fullfill the requirement and get answers or the speak unsecure and do not receive any reply.
Hence, e.g. OPC UA server app needs to talk in a secure manner toward device_admin...which is provide in the updated app.

In addition the communication of the WinStudio located OPC UA client and (ctrlX CORE placed )OPC UA server is not fullfilling the security standards regarding the security-politics. the client does not talk the "security-languages" the server offers.
Unfortunatly the client security features are not update-able yet. Unsecure communication inbetween both OPC UA is only feasible which is not acceptable in many cases. 
Further info available:
https://www.unified-automation.com/news/news-details/article/user-authentication-token-exploit.html
https://apps.opcfoundation.org/ProfileReporting/index.htm?ModifyProfile.aspx?ProfileID=45f01bb8-4a15-44f0-94ac-ff28f15869a5

In case the WinStudioHMI is supposed to ignore that security standards - WinStudio can be most likely enabled to get permission to the datalayer-data by operating with a modified OPC UA server app. That needs to be checked/tested and judged seperately and in dialog with the corresponding R&D colleagues/application.

Best reply by CodeShepherd

Please check the system clocks from your ctrlX CORE and your HMI or engineering PC. They have to be the same for correct security checks.

Also with WinStudio included in IW 15V10 is still a bug in the certification tool. You would need the actual IW15V12 with WinStudio runtime 7.4 SP2 on the HMI PC.

At last please beware that the name of the HMI PC has to be insert in the certificatehttps://files-eu-central-1.t-cdn.net/files/ylAZntDngAQuiUhTicFQm .

WinStudio - certificate setting

 

View original