WebVisu error

I am encountering an issue while attempting to utilize WebVisu within the PLC Engineering software. Upon accessing the visualizations, I see the following error message: "An error happened; will automatically restart". Additionally, the PLC log displays the error: "Opening the communication channel failed".

I would greatly appreciate any assistance in resolving this matter. Please provide any relevant troubleshooting steps or guidance that could aid in rectifying this issue.

Thank you in advance for your time and consideration.

Best reply by Lide

Hello ChrisNichoย 

Yes, I was able to resolve it! I simply deleted the "Visualization Manager" and recreated it.

I tried several other solutions from online forums but none of them worked. Deleting and recreating the 'Visualization Manager' was the only thing that fixed the issue.

I hope this helps you resolve the issue.