ctrlX Drive as a CoE Slave drived with Softmotion

Hello all,

We have a customer who is driving a ctrlX Drive with EtherCAT CoE through an Innovance PLC using the CiA 402 protocol with Softmotion,

The problem is when he uses the MC_PowerON Block, in the CiA 402 protocol the bits 0,1,2 and 3 should remain to TRUE (following a sequence) if we want to go from Ab to AF, however in this case just the bits 0, 1 and 2 are TRUE so is not possible for the axis to go from Ab to AF,

I have tried to do the same thing with a ctrlX Core driving a XCS with CoE and Softmotion and the same happens, so when I activate the inputs of the fb nothing happens,

If I try to activate the Drive via the control word directly or via PLC Open it works so it seems that is a problem of Softmotion,

Does someone know how can I proceed?

Many thanks,

Best reply by JordiLaboria

Good Afternoon, Regarding this issue, the problem seems to come from the status check of the parameter 0x6061 with respect to 0x6060.

The internal bit _bCheckOpMode manages this option and if it is disabled the system boots without problems. (SoftMotion MC_Power)

ย 

At the moment and to solve the problem, the following program lines are implemented. This allows you to use Sotfmotion's MC_Power.

ย 

Really, this whole system of "Fast commissioning" and implementation of ctrlX Core / ctrlX Drive is a real drama... failures here... failures there

ย 

Best Regards

Jordi Laboria

E-Mail: [email protected]

https://www.youtube.com/channel/UCzE-ieCIkyMsuvyE0UDji9g

DCET/SLF4-ES

View original
2
7 replies