Asynchronous motor without Encoder with Motion APP

Hello,

we are trying to run a asynchrunous motor without a Encoder on a XMS2-W0016ANN and a ctrlX CORE wiht Motion App 1.18.2 via SoE.

We configured the axis and the axisprofile, linked them and set the EtherCAT Adress (see Screenshots).

In the Drive engineering we set up a Asynchronous Motor without encoder and set all operation Modes to "Velocitycontrol" (no other Modes are available with this configuration).

When i want to set the motion app to "Run" i get the error "091F0051/0C550185 (see Screenshot).

The EtherCAT is fully operational and has no fault.

I tried to set the encoder interface to "XG20" and  encoder 1 to "no Encoder" but when i want to set the drive to Operational i get a endoder fault "C1112". 

When the interface is set to "no assignment" the drive can be set with the Drive engineering to Operation Mode wihtout a fault. 

I tried to find a option where i can set the Motion app to the "Velocity control" operation mode but i couldn´t find one.

Does anybody has a idea how to solve this problem an get the motor running?

Thanks.

Max

 

Best reply by CodeShepherd

As cyclic position control lagless is the main and mandatory operation mode for our ctrlX MOTION your usecase is not possible right now, as the ctrlX DRIVE cannot be set up accordingly.

By the way, in the ctrlX IO Engineering you would have to look to the startup parameters of the SoE slave, as for a ctrlX DRIVE the main operation mode in standard will be set there to position lagless.

View original
Motion App Axis Profile.PNG
22.47KB
Fehlerlog.PNG
79.05KB
Geber Fehler.PNG
74.73KB
Encoder config.PNG
46.33KB
Motion App Axis.PNG
54.47KB
4 replies