09/26/2025
Setup an Emerson AVENTICS AV with ctrlX OS device with Ethernet/IP
This How-To describes the integration of a Emerson AVENTICS Ethernet/IP AV valve system into ctrlX OS. Other Emerson AVENTICS Ethernet/IP valve systems can also be commissioned in this way.
Step-by-Step guide
Step 1:
First, the Ethernet/IP scanner must be installed and integrated into CODESYS. To do this, follow these instructions:
CODESYS fieldbus add-on installation guide for ctrlX AUTOMATION
Step 2:
If the Ethernet/IP scanner is configured, the ctrlX PLC engineering should look like this:
Illustration 1 Initial state after setting up the Ethernet/IP scanner
Step 3:
Install the description file (EDS file) of the AES Ethernet/IP unit, if this has not already been done. See Tools->Device Repository... click.
Illustration 2 Installing the Device Description File (EDS)
In the window that opens, click Install.. button, select the description file (EDS File) of the AES Ethernet/IP and install it.
Illustration 3 Install Device Description File (EDS)
After installation, the window should look like this.
Illustration 4 Device description file installed
Step 4:
After installing the device description file, the device should be connected to the controller and an IP address should be assigned in the Ethernet/IP scanner subnet. Then the system can be scanned.
Illustration 5 Scan Ethernet/IP devices
If the device is found as in the following image, it can be transferred to the project by pressing "Copy All Devices to Project".
Illustration 6 Scanning Devices Result
Step 5:
After the devices have been transferred to the offline configuration, this must be transferred to the online configuration and the PLC must be switched from STOP to RUN to check whether the communication is working correctly.
Illustration 7 AV Ethernet/IP unit adopted in configuration
Illustration 8 Data transferred to online configuration, PLC to STOP
Illustration 9 Data transferred to online configuration, PLC to RUN