02/26/2025
How-to | Safety
SAFEX FSoE communication between two ctrlX CORES
1 Introduction
This How-to describes how FSoE communication between FSoE devices in different EtherCAT networks can be implemented. The SAFEX #1 is the only EtherCAT device below the ctrlX CORE #1 and is configured as the FSoE master.
SAFEX #2 is the only EtherCAT device below the ctrlX CORE #2 and is configured as an FSoE slave.
The mapping of the FSoE data between the CORE #1 and CORE #2 is implemented via Network Variable Lists (NVL). The configuration of the NVL is very simple and can therefore be recommended.
The How-to basically describes the configuration of the NVL in the PLC programs of the CORE #1 and CORE #2. All programs of the CORE #1 and CORE #2 as well as the programs of the SAFEX #1 and SAFEX #2 are available for download.
Configuration of the NVL in the PLC programs
1.1    Configuration PLC-program CORE #2
The SAFEX #2 is configured as FSoE-Slave. In preparation for mapping the FSoE data, a byte array is declared at the output address %QB0.
Image 1 2: SAFEX #2 is FSoE Slave
The configuration of NVL always starts on the sender side. A name (NVL_Core2toCore1) is defined there and the IP address (192.168.1.1) to which data is to be sent is also specified.
Image 1 3: CORE #2 NVL configuration as Sender
In preparation for mapping the FSoE data, a byte array is declared at the input address %IB0. That means this Input Array of CORE #2 should be send to CORE #1.
Image 1 4: FSoE SlaveInput declaration as Byte-array
Image 1 5: Define an Export file NVL_Core2toCore1.gvl
1.2    Configuration PLC-program CORE #1
The SAFEX #1 is configured as FSoE-Master. In preparation for mapping the FSoE data, a byte array is declared at the output address %QB0.
Image 1 6: SAFEX #1 is FSoE Master
Image 1 7: Choose the exported file NVL_Core2toCore1.gvl for import
Image 1 8: After import we see the imported variable FSoE_
Image 1 9: Mapping the NVL FSoE SlaveInput to FSoE MasterOutput
Image 1 10: CORE #1 NVL configuration as Sender
Image 1 11: FSoE MasterInput declaration as Byte-array
Image 1 12: Define an Export file NVL_Core1toCore2.gvl
1.3    Finish configuration PLC-program CORE #2
Image 1 13: Choose the exported file NVL_Core1toCore2.gvl for import
Image 1 14: After import we see the imported variable FSoE_MasterInput
Image 1 15: Mapping the NVL FSoE MasterInput to FSoE SlaveOutput
PS: How-to created by Dias; Current contact: Thoomas