How To | Safety | FSoE | CODESYS EtherCAT

SAFEX-C and FSoE Communication with ctrlX CORE and CODESYS EtherCAT Master

Overview

This article describes a validation test and example for operating a SAFEX-C.15 as an FSoE Master (FSoE MainInstance) together with the CODESYS EtherCAT Master (EtherCAT MainDevice, Softstack) on a ctrlX CORE. It covers all configuration and programming steps required to establish FSoE communication between the SAFEX-C.15 and the SAFEX-M.02 safety I/O module.

Prerequisites

Hardware and software components used

  • ctrlX CORE X5 with ctrlX OS 4.6.1

  • ctrlX PLC Engineering 4.6.1

  • CODESYS EtherCAT Master package 4.8.2.0

  • SAFEX-C.15 with FW 1.0.1.65 FPGA 227

  • ctrlX SAFETY Engineering 1.8.7.10917

  • EC-BK-12 bus coupler with I/O modules

  • SAFEX-M.02 safety I/O module

Test setup (EtherCAT communication)

ctrlX CORE X5 (XF12) >> SAFEX-C.15 >> EC bus coupler with IO modules and with SAFEX-M.02 safety IO module

Downloading and Installing the SW Components

All software components available via ctrlX OS Store or Collaboration Room.

For the "CODESYS EtherCAT Master" component, the "CODESYS EtherCAT 4.8.2.0.package" must be downloaded, installed and the "ctrlX OS License - CODESYS - EtherCAT Master (add-on)" license purchased and installed on the ctrlX CORE.

Steps

Step 1: Configure the Network Interface on ctrlX CORE X5

In the ctrlX OS WebUI, navigate to "Settings > Network Interfaces" and enable and configure a suitable interface for EtherCAT communication, for example XF12.

Network interface XF12 configuration on ctrlX CORE X5

Step 2: Install and add CODESYS EtherCAT to the PLC Project

Note: A ctrlX I/O Engineering project is not required for this use case. The CODESYS EtherCAT Softstack is used instead of the ctrlX CORE's built-in EtherCAT Master.

Install the "CODESYS EtherCAT 4.8.2.0" package via "Tools > Add-on installer…" in ctrlX PLC Engineering. A detailed guide is available in the ctrlX AUTOMATION Community as a How-To: CODESYS fieldbus add-on installation guide for ctrlX AUTOMATION.

Note: Although that guide covers EtherNet/IP, the same procedure applies analogously to EtherCAT.

Afterward, the EtherCAT Master is added to the PLC project.

CODESYS EtherCAT Master in the PLC project

Step 3: Assign the XF12 Interface to the CODESYS EtherCAT Master

Assign the ctrlX CORE XF12 interface to the EtherCAT Master in the "General" settings tab of the EtherCAT Master. Use "Select…" if necessary to choose the correct interface.

XF12 interface assigned to CODESYS EtherCAT Master

Step 4: Add EtherCAT Devices

Add EtherCAT devices to the EtherCAT Master either manually or by using "Scan for Devices…". In this example, the SAFEX-C.15 and the EC bus coupler with I/O modules and the SAFEX-M.02 safety I/O module are added.

Note: If required, install missing EtherCAT device descriptions beforehand under "Tools > Device Repository…" (ESI files).

Scan for Devices result at EtherCAT Master

Step 5: Add FSoE Devices

The SAFEX-M.02 safety I/O module is an FSoE SubInstance (FSoE Slave). Its FSoE object is added automatically.

Note: The FSoE address of the I/O module must be set via the side rotary switch before installation into the I/O station. In this example, the SAFEX-M.02 module has address "1".

SAFEX-M.02 on the bus coupler with FSoE object

The SAFEX-M.02 has two bytes of safe data inputs and outputs.

I/O addresses of safe data for SAFEX-M.02 (FSoE SubInstance)

Step 6: Add FSoE Connection on the SAFEX-C.15 (FSoE MainInstance)

The SAFEX-C.15 safety controller is also the FSoE MainInstance (FSoE Master). An FSoE connection with "2 Bytes In/2 Bytes Out" for the SAFEX-M.02 must be added using "Plug Device…".

FSoE connection selection for SAFEX-M.02 on SAFEX-C.15

I/O addresses of safe data from SAFEX-C.15 (FSoE MainInstance) perspective

Step 7: Map FSoE Frame Data in the PLC Project

The mapping of input and output data of the FSoE frame between the FSoE Master and Slave is performed by two assignments within the PLC project.

  • _FSoE_MInst_SAFEX_C_Output := FSoESInst_SAFEX_M02_Input; — Mapping FSoE data from SInst to MInst

  • _FSoE_SInst_SAFEX_M02_Output := FSoEMInst_SAFEX_C_Input; — Mapping FSoE data from MInst to SInst

Note: For the ctrlX CORE's EC Master, a simplified alternative is available via the "Slave to slave" dialog tab, which does not require explicit programming.

As a practical example, a new program "prECM_Slave2Slave_Copy" was created under the "EtherCAT_Task":

FSoE frame mapping in the PLC project

The correct hardware addresses for the respective inputs and outputs must be taken from the corresponding data areas (see screenshots above).

Note: In total, 8 bytes of data are exchanged for 2 bytes of safe data (+ 1 byte command, 2 bytes CRC, 2 bytes connection ID, 1 byte for byte alignment).

Step 8: Import SAFEX-M.02 into ctrlX SAFETY Engineering

First, the SAFEX-M.02 must be added to ctrlX SAFETY Engineering via ESI import in the Slave Device Editor.

ESI import of SAFEX-M.02 in the Slave Device Editor

Step 9: Configure the FSoE Object in the Safety Project

In ctrlX SAFETY Engineering, add the FSoE module to the project in the "Terminal Scheme", configure the correct profile, and set the correct slave address.

FSoE object SAFEX-M.02 configuration in Safety project

In the example, the hardware inputs and outputs are connected to the SAFEX-M.02 module both on the hardware and software side.

Functional Scheme test example with SAFEX-M.02 in Safety project (1)

Functional Scheme test example with SAFEX-M.02 in Safety project (2)

Conclusion

Following these steps, the SAFEX-C.15 operates as an FSoE Master using the CODESYS EtherCAT Softstack on the ctrlX CORE X5, with FSoE communication established to the SAFEX-M.02 safety I/O module via the EC bus coupler.