02/20/2025
How-to

How-to use TB option (STO function activated over safe fieldbus) at ctrlX DRIVE

What the function is good for

If using the function "Safe Torque Off over safe fieldbus" coming with the "TB" hardware option, the following functions are included:

  • Safe Torque Off (STO)

  • Safe Stop 1 time monitored (SS1-t)

  • Safe Brake Control (SBC) (at activation of STO function)

The selection of the safety functions is taking place over one of the following safe fieldbuses

  • Fail Safe (FSoE) over EtherCAT SoE or EtherCAT CoE
    or

  • PROFIsafe on PROFINET

Fig. 1: Functional overview of SS1-t and STO function

Versions used

All the functions and screen shots are based on:

  • ctrlX DRIVE Engineering version 01V32

  • Runtime / Firmware version of drive AXS-V-0604

Prerequisites

A connection to the various ctrlX DRIVE has been successfully established, the devices are correctly wired and 24 V are successfully put on. As well the engineering tool ctrlX DRIVE Engineering has been started.

1. Function

The function follows the following scheme:

SS1-t (time-prioritized, PLC/NC-controlled transition to standstill)

If the bit SS1 is activated, a time monitoring is started. Within this time the drive should be decelerated by the control system to arrive at standstill. Latest after this time the "Safe Torque Off" (STO) function and the "Safe Brake Control" (SBC) gets active.

If axis is arriving in standstill condition the drive can already be switched from AF (drive enable) to Ab (drive dis-enabled) and the "Safe Torque Off" (STO) function activated.


Safe Fieldbus interaction

One needs to select the so called "Safety Drive Profile V1"

Fig. 2: Safety Drive Profile V1


and thus would get the following interchange signals in between control and drive:

Fig. 3: Consumer / Producer connection (control / status word)

2. Parameterization in drive

The axis must be parameterized in the following sequence:

Fig. 4: Activation of safety function
Fig. 5: Start "Initial commissioning"
Fig. 6: Assign password (in here password "Safety" is used)
Fig. 7: Assign and write axis identifier
Fig. 8: Apply axis identifier
Fig. 9: Parameterize "Safe brake control (SBC)"

If a brake is present, check the checkbox, if not uncheck it like shown in here.

Fig. 10: Parameterize "Safety bus communication"
Fig. 11: Write slave address (in here: FSoE slave address)
Fig. 12: Confirm slave address
Fig. 13: Select profile "Safety Drive Profile V1 (791/796)"
Fig. 14: Set the "Time to STO" to a proper value according to your application (with some safety margin)
Fig. 15: Create, name and save so called "SafeMotion report" (contains all information for eventual later change of devices at break down (should be put to machine documentation))
Fig. 16: For lateron change of parameterization the menus can be accessed directly

If you like to react as fast as possible on the selection of SS1/STO function w/o delay time of the safe bus communication the following parameterization may be used:

Fig. 17: I/O settings (for direct and quick reaction to SS1/STO selection)

Mind that pins XG31/3 and XG31/8 must be connected (wired)!

The E-Stop function in this case needs to be activated.

Fig. 18: E-Stop function to be made active (in case of direct and quick drive reaction to SS1/STO selection)

3. Parameterization in SAFEX C.xx safety control

The parameterization is done according to the following:

Install device file in "Slave Device Editor" of ctrlX SAFETY Engineering.

Fig. 19: Install device file (1)
Fig. 20: Install device file (2)

Hint: The relevant device files can be found in the installation of ctrlX DRIVE Engineering, usually under "...\Program Files (x86)\Rexroth\ctrlX DRIVE Engineering\DeviceDataSheets", see e.g.:

Fig. 21: Usual location of DeviceDataSheets

Create a project:
- Insert ctrlX DRIVE in "terminal scheme" of SAFEX project
- Activate "Safety Drive Profile V1" and define the FSoE address and connection ID
- Insert needed Safety switches like STO and SS1 to the project according to your needs

Fig. 22 : Add ctrlX DRIVE in SAFEX project (terminal scheme)

Insert "2Byte Safety Drive Profile V1 (791 - 796)" to "functional scheme" of project and connect the corresponding STO and SS1 switch to the corresponding signals of the function block.
Download the safety project to the SAFEX control hardware after compilation and activate it after going online.

Fig. 23: Function block of "Safety Drive Profile" in "functional scheme"


4. Parameterization in control system

The parameterization is done according to the following:

Install device description with new "Safe Drive Profile V1" module in ctrlX CORE I/O Engineering.

Fig. 24: Install device description to ctrlX CORE I/O Engineering

Scan for EtherCAT devices and add to project.

Fig. 25: Scan for devices
Fig. 26: Add to project

Plug 2Byte Safe Drive Profile module to drive and 2Byte in / out module to SAFEX!

Fig. 27: Plug 2Byte Safe Drive Profile module to the drive and 2Byte in / 2Byte out module to SAFEX

Copy FSoE telegrams from FSoE master to FSoE slave and vice versa and download the project to ctrlX CORE.

Fig. 28: Copy FSoE telegrams from FSoE master to FSoE slave and vice versa

When the SS1 function is activated by the E-Stop button the drive needs to be decelerated and the drive disenabled (AF --> Ab). Therefor the SS1 bit in the FSoE telegram is checked via PLC which disenables the drive when SS1 is activated.

Fig. 29: ctrlX CORE PLC Engineering


A usual scope reading is looking like the following:
1. Activation of SS1 function --> drive will decelerate by switching from AF --> Ab.
2. SS1 is active.
3. Drive is in Ab.
4. STO is active.

Fig. 30: Scope readings with usual sequence
3