02/18/2025
How To use Safe Door Lock (SDL) function with ctrlX DRIVE (with Safe Motion (SMO) hardware option "M8")
What the function is good for
If using the Safe Motion (SMO) M8 hardware option, the function Safe Door Lock (SDL) allows to create the necessary safe functions for one individual drive and thus one safe area.
The safe state information are used to control a safe door device with the use of the I/O mapper logic.
Fig. 1: Function block Safe Door Lock (SDL)
Mind: The drive must be equipped with Safe Motion (SMO) M8 hardware option!
Versions used
  • ctrlX DRIVE Engineering version 01V32
  • Runtime / Firmware version of drive AXS-V-0604
A connection to the various ctrlX DRIVE has been successfully established, the devices are correctly wired and 24 V are successfully put on. As well the engineering tool ctrlX DRIVE Engineering has been started.
1. Function
The function follows the following scheme:
EMERGENCY STOP (SMES)
If the EMERGENCY STOP button is pressed, the corresponding safety function is activated immediately, which leads to a deceleration of a still moving axis. After coming to standstill and acknowledging the EMERGENCY STOP function the drive is shut off and thus torque/force free. The door is released to be opened at that time.
Note, that the “Drive Enable” signal from the control has to be removed before the time entered for the reaction time of the EMERGENCY STOP function is exceeded, thus directly after the standstill is accomplished. Otherwise an error is shown.
If the EMERGENCY STOP button is released again and the door is shut again the Reset button needs to be shortly pressed that the EMERGENCY STOP and thus the function is released again as well. Then the drive can be activated (drive enable be set) again.
Mind that after first time switching on of the devices the Reset button needs to be shortly pressed to initially make the execution of the safe function work.
Mind that the EMERGENCY STOP is always prior to all other safety functions and, if activated, superseding the in before active safety function.
Mode Select - Change to Safety Operation Mode (activating the safe operational stop (SMST2))
If the “Mode Select” is switched, the corresponding safety function at the drive is activated immediately, which leads to a deceleration of a still moving axis. After getting to standstill the drive is in operational stop with torque/force on. The door is released to be opened at that time.
If the Mode Select switch is released again and the door is shut again the Reset button needs to be shortly pressed in order that the safe function SMST2 is released again.
Enabling Control (activating safe motion with limited speed)(SMM1 or SMM2)
If the “Enabling Control” button is pressed additionally to the “Mode Select” switch, the corresponding safety function SMM1 or SMM2 at the drive is activated immediately, which allows the control to set a command with reduced speed. If the “Enabling Control” button is released again the safe operational stop (SMST2) is getting active again.
Switchover of reduced limited speed (SMM1 to SMM2)
If the “Switchover SMM1 to SMM2” switch is activated, the corresponding safety function SMM1 or SMM2 at the drive is switched over immediately, which allows the control to set a command with a corresponding reduced speed.
2. Wiring of drives
The wiring should be according to the following principles:
Fig. 2: Wiring schematics
3. Parameterization
The axis must be parameterized like the following:
Fig. 3: Settings of "Local safety zone"
The safe inputs need to be set according to the requested functionality. In here they are set to the following:
  • Safe input 1: EMERGENCY STOP
  • Safe input 2: Mode selection signal (to change to safe operation mode)
  • Safe input 3: Enabling control signal (Enabling pendant)
  • Safe input 4: Switchover from Safe operation mode SMM1 to SMM2 allowing different safe limited speeds to be selected.
  • Safe input 5: Acknowledgement that door is closed and locked
Fig. 4: Settings of "Signal control of inputs"
The safe outputs need to be set according to the following:
Fig. 5: Settings of "Signal control of outputs"
The I/O mappers should be set according to the following:
Fig. 6: Settings of "Network 1"
Fig. 7: Settings of "Network 2"
Fig. 8: Settings of "Network 3"
Fig. 9: Settings of "Network 4 "
Fig. 10: Settings of "Network 5"
Fig. 11: Settings of "Network 6"
Fig. 12: Settings of "Network 7"
Fig. 13: Settings of "Network 8"
The I/O settings need to be parameterized according to the following:
Fig. 14: Settings of "I/O" signals
Mind that at first switching on one might get an error at the local safe area master:
In using the normal "Reset" function of the drive (not the one for "Reset" of the safety functions) this can be quit.
Parameter_Test_SDL_Axis_1.zip
203.09KB
Safety