08/19/2025
How-To, Safety, ctrlx SAFETY, Controls, SAFEX, Safe Data
How to determine which SAFEX safe data exchange method should be used
Content
In this How-To we will show you three safe data exchange methods and help determine which one may be best for your application
Things to consider
  • Is there an EtherCAT network?
  • Are SAFEX-C.1x controls in the same EtherCAT network or different EtherCAT networks?
  • Is there more than one ctrlX CORE?
  • Is there a SAFEX-C.12 or a SAFEX-C.15?
  • Number of SAFEX-C.1x controllers?
  • Amount of safe data exchange needed?
  • Project management, is there one or more ctrlX SAFETY Engineering projects?
Fig. 1.: Things to consider flowchart
SAFEX-C.12-to-SAFEX-C.12 two safe data exchange methods
  1. Safety over EtherCAT (FSoE) on Ethernet Interface 1 XF28/XF29 (Primary), same EtherCAT network
  2. Safe MainInstance-to-MainInstance Communication (SMMC) over EtherCAT Automation Protocol (EAP) on Ethernet Interface 1 XF28/XF29 (Primary), different EtherCAT networks
Fig. 2.: SAFEX-C.12-to-SAFEX-C.12 two safe data exchange methods
SAFEX-C.15-to-SAFEX-C.15 three safe data exchange methods
  3. Safe MainInstance-to-MainInstance Communication (SMMC) over TCP/IP Ethernet Interface 2 XF30/XF31 (Secondary), no EtherCAT network needed
Fig. 3.: SAFEX-C.15-to-SAFEX-C.15 three safe data exchange methods
SAFEX-to-SAFEX safe data communication methods:
1. Method #1 FSoE (SAFEX-C.12/SAFEX-C.15)
  • Up to 8* ctrlX SAFETY controllers via Safety over EtherCAT FSoE (maximum 228 bytes per direction)
  • Allows connection within single EtherCAT network (ctrlX CORE/EtherCAT MInstance)
  • 96 input/output bits per controller
  • SubInstance-to-SubInstance data must pass through master controller
  • Separate ctrlX SAFETY Engineering Projects for each SAFEX controller
  • FSoE between ctrlX SAFETY controllers extends and scales capacity
    • in CPU power and
    • Number of I/O
Fig. 4.: SAFEX-to-SAFEX safe data exchange Method #1 FSoE (SAFEX-C.12/SAFEX-C.15)
2. Method #2 SMMC over EAP on Ethernet Interface 1 XF28/XF29 (SAFEX-C.12/SAFEX-C.15<->SAFEX-C.12/SAFEX-C.15)
  • Up to 4 ctrlX SAFETY controllers via Safe-MInstance-to-MInstance-Communication (SMMC) over EtherCAT Automation Protocol (EAP)
  • Allows connection between different EtherCAT networks (ctrlX CORE/EtherCAT MInstance)
  • 32 output bits per controller
  • Participants can read all controller output bits (no passing of data through an EtherCAT controller)
  • SMMC participant status can monitored
  • Single ctrlX SAFETY Engineering Project for all SAFEX controllers
  • SMMC between ctrlX SAFETY controllers extends and scales capacity
    • in CPU power and
    • Number of I/O
Fig. 5.: SAFEX-to-SAFEX safe data Method #2 SMMC over EAP on Ethernet Interface 1 XF28/XF29 (SAFEX-C.12/SAFEX-C.15<->SAFEX-C.12/SAFEX-C.15))
3. Method #3 SMMC over TCP/IP on Ethernet Interface 2 XF30/XF31 (Secondary), SAFEX-C.15 only
  • Up to 8 ctrlX SAFETY controllers via Safe-MInstance-to-MInstance-Communication (SMMC) over TCP/IP
  • Allows a standalone connection between SAFEX-C.15 controllers without an EtherCAT network or independent of the EtherCAT network
  • SMMC participant status can be monitored
    • in CPU power and
    • Number of I/O
Fig. 6.: SAFEX-to-SAFEX safe data Method #3 SMMC over TCP/IP on Ethernet Interface 2 XF30/XF31 (Secondary), SAFEX-C.15 only
Summary
Fig. 7.: SAFEX-to-SAFEX safe data exchange method summary
* Maximum FSoE data is 228 bytes. If other FSoE devices are used in the network this value is reduced
Additional Resources
3
Safe Data Exchange with SAFEX.pdf