05/12/2026
How-to | Drives | Engineering

How-to connect Bonfiglioli AxiaVert inverter to ctrlX OS devices via EtherCAT

Requirements

Hardware

Software

  • EtherCAT ESI Files for Bonfiglioli AxiaVert

  • ctrlX I/O Engineering

  • ctrlX OS V2.6.4 (or higher)

Get and install ESI Files

  • Download ESI Files for AxiaVert from the Bonfiglioli website.

  • After downloading the file. install ESI Files in ctrlX I/O Engineering software.

  • Open menu Tools -> Device Repository.

Device Repository

 

  • Click Install

Figure 2: Install device

 

  • Select BD_Axia.xml file and then press Open.

Figure 3: AxiaVert ESI file

  • Device Repository window can be closed.

 

Online configuration

  • If the AxiaVert is connected to ctrlX OS, online configuration can be used.

  • Online configuration automatically scans the topology of the system. Devices are automatically detected and set in the hardware configuration.

  • Right-click on ethercatmaster -> Scan for Devices.

Figure 4: Scan for Devices

  • Import found devices into the project and click OK.

Figure 5: Scan for Devices - Result
  • ethercatmaster is now populated with founded devices

Figure 6: Scan for Devices - Device tree

 

  • Plug device

  • Default PDO configuration is Velocity mode, the user can change default mapping changing the plug device.

  • To do that right click on the Axis -> Plug Device

Figure 7: Plug Device

 

  • Select the desired PDO map and then click “Plug Device”.

Figure 8: Plug Device - Modules

  • The hardware configuration is automatically updated.

Figure 9: Plug Device - Device tree

 

  • Change PDO map

  • The user can manually change the PDO map. To do that double click on the AxiaVert Single Axis and enable the Expert settings.

Figure 10: Expert settings
  • In the Expert Process Data tab select the desired PDO List (e.g. 16#1600 – CSP Outputs) and then click Insert

Figure 11: Manual PDO map - Insert

 

  • Select the desired object (e.g. 16#6060:16#00 – Mode of Operation) and click OK.

Figure 12: Manual PDO map - Object selection

  • PDO content list is now updated.

Figure 13: Manual PDO map - Result

  • Download the project to the controller

Figure 14: Download project

ctrlX OS configuration

  • Axis Profiles

  • Log in in ctrlX-OS and add Axis Profiles.

Figure 15: Axis Profiles
  • Select the fieldbus device to associate to the axis profile

Figure 16: Axis Profiles - Fieldbus selection

  • Edit the axis profile to set the correct scaling.

Figure 17: Axis Profiles - edit

  • In the Scaling section select Manual configuration

Figure 18: Axis Profiles - Manual configuration

  • Set the parameters:

    • Type: Rotary

    • Resolution: 65536

    • Numerator: 1

    • Denominator: 1

  • And click Save

Figure 19: Axis Profiles – Scaling parameters Axes

  • Associate the axis profile to the real axis by editing it

Figure 20: Axes - Edit

  • In General section:

    • Select the correct profile in the Connection to physical drive field

    • Set Type as Rotational Drive

    • Set Axis Positioning as Absolute

  • And click Save.

Figure 21: Axes - Parameter (I)

Figure 22: Axes - Parameter (II)

  • Run the system

  • Set the system in Running. 

Figure 23: Run the system

  • If the configuration is correct, Motion switched to running message should appear.

Figure 24: Run ok

  • Test the system

  • Once the system is up and running, AxiaVert can be tested via ctrlX-OS, without the need to write code.

  • In the Commissiong section of the Axes, the drive can be powered on and put, for example, in jog mode.

Figure 25: Commissioning

Figure 26: Commissioning - Power on

 

Figure 27: Commissioning - Set jog parameters

 

Figure 28: Commissioning - Run jog

 

The Company

Bonfiglioli is a worldwide designer, manufacturer and distributor of a complete range of gearmotors, drive systems, planetary gearboxes and inverters, which satisfy the most challenging and demanding needs in industrial automation, mobile machinery and renewable energy. The Group serves more industries and applications than any other drives manufacturer and is a market leader in many sectors; its three business areas - Industry & Automation Solutions, Mobility & Wind Industries, Selcom Group - embody all the expertise and experience acquired over the years in the respective industries. Established in 1956, Bonfiglioli operates worldwide in 80 countries with 23 commercial sites, 17 production sites, a wide distribution network comprising more than 550 partners, and can count on 5.000 professionals. Excellence, innovation, and sustainability are the drivers behind the growth of Bonfiglioli as a company and team and represent the guarantee of the products and services quality offered its clients.

 

Types