Mapping Assembly instances - Ethernet/Ip

Hello dear folks,

I am trying to stablish connection between AB plc as Ethernet/Ip-Scanner (L5555 with RSLogix5000 v16) and the CtrlX-Core as the Ethernet/Ip-Adapter.

Since this AB plc is super old, I am not able to import any EDS file into my project, and therefore I have to use Generic Ethernet Module instead, and then, map the Assembly instances of Input, Output and Configuration inside the RSLogix5000 project.

Could you inform me the addresses that are used by the CtrlX-Core? The IndraDrive uses 102, 101 and 110 (Input, Output and Configuration), but I believe it is not the same addresses.

Please, check the screenshot below. ๐Ÿ™‚

Thanks a lot

ย 

Best reply by GustavoTaffarello

Hello dear folks,

Great news. I have successfully communicated the CtrlX-Core with the AB-plc using the Codesys Ethernet/Ip version 4.2.0.

Over the past days I could not stablish a solid connection using the package version 4.4.0. The CtrlX-Core (adapter) was constantly opening and closing the port with the AB-plc (scanner), and I could check that on the CtrlX-Core log book as well.

Is this a known bug on the Codesys package 4.4.0?

Please, take a look at the video here attached.

Thanks

AB and CtrlXCore using Eip.mp4
6.3MB
View original
4 replies